高楼连廊的防火门

总高26楼的连廊消防门是常闭防火门可以允许孩子们自由出入吗?常闭防火门的安装标准有没有必须加门禁系统,谢谢

小亮救援队 | 2025-06-17 16:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

小唐12321 2025-06-17 17:06 00 [回复]举报

正常都是常闭,为什么不能出入,加不加门禁看你管理啊,一般一楼跟顶楼需要加门禁,门禁记得联动时候能断电打开就可以。

李勤 2025-06-17 17:24 00 [回复]举报

首先不是经常走人的通道就是常闭防火门,处于日常管理可以加门禁,但是添加门禁火灾时能自动打开,现场能手动开启。

牛丫头消防课堂 2025-06-17 21:18 00 [回复]举报

按照你说的,连廊处常闭防火门比较合适,允许人通行;

很多单位加门禁,是为了安全考虑,害怕连廊区域人高处坠落。

你如果加门禁,一定注意一个原则,你这里是互相作为第二个安全出口的连廊,那么加了门禁,必须不能影响双方的人员疏散,不能按照一个单元设置门禁,因为连廊属于公共疏散区域。

门禁处理不好,影响疏散,就是人为责任。