消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

火灾自动报警系统联动测试的频次

请问刘亦菲吴彦祖们,规范要求的火灾自动报警系统联动测试的频率到底是怎么规定的,目前看下来是1年1次全区覆盖,但大型商业综合体消防安全管理规则里14.3又要求半年做一次。是否遵循GB就合格,XF/T只是推荐性的,不做强制要求,求解,谢谢。

夏枯草 | 2024-10-22 21:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

张治福 2024-10-23 16:44 20 [回复]举报

是的,满足消防法和国标1年1次是最低要求。在此基础上,推荐有条件的大型商业综合体半年1次,也是因为这类大型商业综合体如发生应急事故,损失太大了的原因。

夏枯草   回复: 张治福2024-10-27 13:33

谢谢这位张工。主要是都用的钢卷,还带水喷雾,尺寸大的钢卷测试一次真的劳民伤财,复位什么的,实在是伤不起,然后呢其实除了每年滚动一遍,都是按照GB有定期做卷帘点动和检查的,同时企业内部是每年有检查进行联动抽检的(只是不是全覆盖而已)。

0    0 [回复]举报

王发发   回复: 夏枯草2024-12-20 08:59

请问下哪一个规范规定的消防维保检查怎么覆盖的?

0    0 [回复]举报

王的MIX4 2024-10-24 14:23 10 [回复]举报

一般大型商业体是按照就高原则确定的,毕竟特别法优于一般法。

零几年的风 2024-11-04 17:47 00 [回复]举报

营口山鹰

关闭

关闭

手机APP下载