消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教一下关于高位水箱设置的问题

请教一下关于高位水箱设置的问题,3层及以上单体建筑面积大于10000平方米的其他公共建筑需要设置高位水箱,那么5层单体建筑面积在5000平方米需要设置吗?

悲喜自渡 | 2024-08-01 07:32
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

LHH2737 2024-08-01 09:18 00 [回复]举报

可以不设,但要在消防水池处设置稳压泵一备一用

西湾子消防小能手   回复: LHH27372024-08-01 10:00

设置稳压泵是有效水位满足不了最不利点水压才需要设置的

0    0 [回复]举报

LHH2737   回复: 西湾子消防小能手2024-08-01 10:29

GB 50974-2014第6.1.9.2条:其他建筑应设置高位消防水箱,但当设置高位消防水箱确有困难,且采用安全可靠的消防给水形式时,可不设高位消防水箱,但应设稳压泵;

0    0 [回复]举报

西湾子消防小能手 2024-08-01 09:44 00 [回复]举报


多层公共建筑、二类高层公共建筑和一类高层住宅,不应小于18m³。多层住宅不应小于6m³

你也没叙述清楚建筑使用性质和仅设哪些消防设施

悲喜自渡   回复: 西湾子消防小能手2024-08-01 17:39

使用性质公共建筑,商场。5层18m5000㎡的多层商场,需要设置高位水箱吗?

0    0 [回复]举报

西湾子消防小能手   回复: 悲喜自渡2024-08-02 15:08

要是能满足楼上所说的GB50974-2014第6.19.2条可以不需要设置高位水箱,满足不了就需要按照GB50974-2014第5.2.1.2条要求了

0    0 [回复]举报

消防网友68723 2024-08-01 09:55 00 [回复]举报

其他建筑应设置高位消防水箱,但当设置高位消防水箱确有困难,且采用安全可靠的消防给水形式时,可不设高位消防水箱,但应设稳压泵;
    3 当市政供水管网的供水能力在满足生产、生活最大小时用水量后,仍能满足初期火灾所需的消防流量和压力时,市政直接供水可替代高位消防水箱

关闭

关闭

手机APP下载