消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

厂房排烟风机可以放在室外无风机房,做防火处理么?

上海工厂项目,单层厂房,屋顶为轻钢无法放置风机,需要机械排烟,排烟风机可以放在室外,做防火处理么?

根据上海市《建筑防排烟系统设计标准》4.3.6 ,需要设置专用机房。但根据4.3.6条文解释:当条件受限时,应有防火保护。是否可以参见3.3.5的

条文解释,按照正压送风风机的要求。但是4.3.6条文解释,又多说了一句:工业建筑.....,屋顶式排烟风机可以直接设在室外。这条的意思是不是

说屋顶排烟风机可以直接放在屋顶,无需防火保护,而如果设在其他,比如一楼地面,可以在耐火1小时的保护箱体内。但是条文解释又说这主要是、

民用建筑的屋顶。感觉有点混乱。

云山设计 | 2024-01-06 19:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2024-01-08 08:45 10 [回复]举报

上海建筑防排烟系统设计标准 DG/TJ08-88-2021

3.3.5 机械加压送风风机可采用轴流风机、混流风机或中、低压离心风机等,其设置应符合下列要求:

5 当加压送风风机独立布置确有困难时,可以与排烟补风机合用机房。当受条件限制,需与其它通风机、空调箱合用机房时,除应符合上述专用机房的要求外,还应符合下列条件:        

1)机房内应设有自动喷水灭火系统;        

2)机房内不得设有用于排烟和事故通风的风机与管道。


4.3.6 排烟风机应设置在专用机房内,除应符合本标准第3.3.5条第4款的规定外,还应符合下列规定:    

1 机房内不得设置用于机械加压送风和排烟补风系统的风机与管道。    

2 排烟风机与排烟管道的连接部件应满足280℃时连续工作30min的要求。    

3 当排烟系统风机与通风风机、空调机组合用机房时,机房内应设置自动喷水灭火系统,排烟管道耐火极限应不小于1.0h。



我理解您的问题是厂房顶因承重问题无法布置排烟机房?于是把防烟机房布置在厂房外的地面上?在地面上做一个专用的排烟机房,机房不低于二级耐火等级,按相应要求布置。

潘天坤 2024-06-16 19:42 00 [回复]举报

正文里其实已经作出要求:第3.3.5条第4款有提及什么情况下可以设置在室外,同时第4.3.6条又作出要求“除了参照第3.3.5条第4款外还应”,也就是说排烟机房也是按照加压送风机房规定执行。

关闭

关闭

手机APP下载