民用住宅楼地下室 车位设计问题

这样的设计符合规定吗?如果不合符,有没有参考文献?

一骑绝乘 | 2023-09-09 14:15
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

王家任 2023-09-14 15:15 00 [回复]举报

不合规,电梯候梯厅应与地下汽车库做防火分隔,地库联通住宅的楼梯间应为甲级防火门。

一骑绝乘   回复: 王家任2023-09-28 09:45

非常感谢,电梯房外确实有防火门,在照片里面又转就是门,照片上看不到。楼梯出来照片上也有防火门的。

0    0 [回复]举报

南明离火   回复: 一骑绝乘2023-10-06 16:58

合理,法无禁止皆可为

0    0 [回复]举报

一骑绝乘   回复: 南明离火2023-10-08 16:54

大师啊


0    0 [回复]举报

阳明心 2023-11-09 10:01 10 [回复]举报

《建筑设计防火规范》(GB 50016-2014 <2018版>)规定:

5.5.6 直通建筑内附设汽车库的电梯,应在汽车库部分设置电梯候梯厅,并应采用耐火极限不低于2.00h的防火隔墙和乙级防火门与汽车库分隔。