消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防控制室可以和厂务值班室合用吗

《建筑防火通用规范》全文强制性,消防控制室可以和厂务值班室还能布置在一起吗?

4.1.8 消防控制室的布置和防火分隔应符合下列规定:
    1 单独建造的消防控制室,耐火等级不应低于二级;
    2 附设在建筑内的消防控制室应采用防火门、防火窗、耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.50h的楼板与其他部位分隔;
    3 消防控制室应位于建筑的首层或地下一层,疏散门应直通室外或安全出口;
    4 消防控制室的环境条件不应干扰或影响消防控制室内火灾报警与控制设备的正常运行;
    5 消防控制室内不应敷设或穿过与消防控制室无关的管线;
    6 消防控制室应采取防水淹、防潮、防啮齿动物等的措施。

畅波 | 2023-04-19 17:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

陈曲 2023-04-19 17:27 00 [回复]举报

消控室一般可以和监控室 厂区中控室等合用 他们功能上有交集 或者对消防系统有一定的辅助性 

畅波   回复: 陈曲2023-04-19 17:33

审图已经过了,就怕墙砸掉两个合并验收过不了,还有就是以后的消防检查,安评等验收会有问题。

0    0 [回复]举报

陈曲   回复: 畅波2023-04-20 08:51

个人建议尽快联系设计进行变更,这个问题解决的越早越好

0    0 [回复]举报

畅波   回复: 陈曲2023-05-04 11:03

只要是设计院不愿意改图,说审图单位不同意,审图前沟通过此事。

企业自己改怕影响以后的安评验收。

0    0 [回复]举报

陈曲   回复: 畅波2023-05-08 17:38

厂区监控可以辅助消防口更好的把控现场状况,并不是无关管线,设计院说的根本不成立

0    0 [回复]举报

关闭

关闭

手机APP下载