严重危险级的机房内,为什么配备4公斤二氧化碳手提灭火器

严重危险级场所配置二氧化碳灭火器需要89B以上,89B以上的都是30公斤以上推车式灭火器,那其他灭火效能低的手提式二氧化碳灭火器是不是就不用配备了

旋风2012 | 2022-07-21 16:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

听雨眠 2022-07-22 09:22 00 [回复]举报

机房是E类火灾吧,E类火灾场所的灭火器最低配置基准不应低于该场所内A类(或B类)火灾的规定,用3A或89B可以根据场所的实际情况决定。

旋风2012   回复: 听雨眠2022-07-22 10:09

机房有洁净要求,配置二氧化碳灭火器。严重危险级机房不用配备灭火效能低的手提二氧化碳灭火器。但我去检查发现机房内也配备了手提式4公斤的,不知道什么原因,也找不到依据

0    0 [回复]举报

听雨眠   回复: 旋风20122022-07-22 11:03

他是只配了手提式二氧化碳灭火器,还是有其他灭火措施情况下增配了手提二氧化碳

0    0 [回复]举报