各位老师好,近日网上看到一个大平层的项目。整个户型500多平,采用剪刀梯。规范图示中已经明确,两户的情况下,这种在公区只能到达一个安全出口的做法是不行的。那么请问,如果只有一户,这种做法是否可行。这个项目名位麓辰黑珍珠,应该是比较新的项目。



climbingman | 2022-05-26 18:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

荔枝 2022-05-27 10:49 00 [回复]举报

应该是没问题的,可以将户内考虑成一个大房间,这个房间有两个安全出口直通疏散楼梯;但是从图上看这套户型是跃层的,在二层是否有开设直通疏散楼梯的安全出口,没开的话是不满足户内疏散距离的。

climbingman   回复: 荔枝2022-05-27 11:23

谢谢您的回答,但是还有疑问就是规范图示上也考虑到了公区的疏散问题,这里试想如果在公区的不是本户的用户,而是物业或者电梯检修人员,那么他们在公区一旦发生火灾就只有一个安全出口可以使用

0    0 [回复]举报

荔枝   回复: climbingman2022-05-30 09:56

对于这点确实是有一定的争议,但是在规范中是默认在楼梯内部即为安全区域,也就是这种核心筒其实是不存在消防隐患的公共区。

2    0 [回复]举报

climbingman   回复: 荔枝2022-06-01 00:46

好的,感谢您的回答!