消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防供电设计

电子厂房(丙2项)设有室内外消火栓和自喷,厂房体量2万余立方,按《消水规》室外用水量为30L/S,按《建规》按三级负荷供电,屋顶水箱设稳压泵稳压,可否适用《消水规》6.1.10条当室内临时高压消防给水系统仅采用稳压泵稳压,且为室外消火栓设计流量大于20L/s的建筑和建筑高度大于54m的住宅时,消防水泵的供电或备用动力应符合下列要求:
    1 消防水泵应按一级负荷要求供电,当不能满足一级负荷要求供电时应采用柴油发电机组作备用动力;
    2 工业建筑备用泵宜采用柴油机消防水泵。

消防网友44733 | 2022-04-19 17:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2022-04-19 20:12 10 [回复]举报

消水规6.1.10为不设高位水箱的情况,如设置高位水箱,可不执行此条款。

消防网友78337 2022-04-20 10:38 00 [回复]举报

你的要求本身有问题,或者说代价更大,


水系统设置可能是有所减少设备,但是你建筑整体的消防供电设计要求从三级消防负荷提高到一级消防负荷,多花不少钱。

关闭

关闭

手机APP下载