消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于消防水池有效容积计算

求助大神,假如一栋建筑的火灾延续时间为2h,该建筑设置了防火卷帘防护冷却水幕,水幕持续时间3h,如此的话,计算消防水池设计有效容积时,该栋建筑的消防水池补水量是按2h计算还是3h计算?

小钟打怪兽 | 2021-09-18 15:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

一片冰雨 2021-09-20 21:45 00 [回复]举报

消防规范里面好象一贯是就多不就少吧。否则的话你那个3小时根本就达不到设计要求,就是一个空,怎么可以?

消防网友80490   回复: 一片冰雨2021-09-21 15:04

水池补水量不是根据市政管道补水能力去计算么?

0    0 [回复]举报

一片冰雨   回复: 消防网友804902021-09-22 00:16

一、为啥要设消防水池?

4.3.1 符合下列规定之一时,应设置消防水池:

    1 当生产、生活用水量达到最大时,市政给水管网或入户引入管不能满足室内、室外消防给水设计流量;

    2 当采用一路消防供水或只有一条入户引入管,且室外消火栓设计流量大于20L/s或建筑高度大于50m时;

    3 市政消防给水设计流量小于建筑室内外消防给水设计流量。

二、你在问火灾延续时间啊?

     该栋建筑的消防水池补水量是按2h计算还是3h计算

0    0 [回复]举报

横行霸道的螃蟹 2021-11-03 01:48 10 [回复]举报

3h

关闭

关闭

手机APP下载