吊顶高度大于800mm且内有可燃物时,在吊顶上部增设标准型立式喷头,请问可燃物如何定义?

各位行业专家:吊顶高度大于800mm且内有可燃物时,在吊顶上部增设标准型立式喷头,请问可燃物如何定义?装修木龙骨肯定是,如果是金属龙骨,但是有空调保温(难燃也有铝箔保护层)是否也定义为可燃物呢?谢谢!

zhouzhou | 2021-06-20 12:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

林继青 2021-06-20 13:15 10 [回复]举报

金属龙骨不属于可燃物,增加保护不影响本身的燃烧性能