请教各位大咖,我单位消防控制室的应急电源控制柜坏了,但是各个楼层的疏散指示牌都是正常的,但好多公司说如果要更换新的控制柜(品牌更换了),同步必须更换与控制柜同品牌的疏散指示牌,是这样的吗?感觉太浪费了。求解。

邹健康 | 2025-05-08 08:13
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

EHS专家-DL 2025-05-08 12:10 00 [回复]举报

是否需要更换灯具取决于技术兼容性,而非品牌一致性‌。尤其是通讯协议、电压等级等技术参数匹配一致就可以啊。

wetom 2025-05-08 17:43 00 [回复]举报

找设备厂家修修控制室的控制柜不就行了,各楼层能亮,是因为还有区域的分配电装置在工作。

牛丫头消防课堂 2025-05-10 00:28 00 [回复]举报

按理说应该兼容,实际很多厂家不兼容

依据《消防应急照明和疏散指示系统技术标准》 GB51309-2018第3.4.1条, 应急照明控制器的选型应符合下列规定:

2 应急照明控制器采用通信协议与消防联动控制器通信时,应选择与消防联动控制器的通信接口和通信协议的兼容性满足现行国家标准《火灾自动报警系统组件兼容性要求》GB 22134有关规定的产品。