请问下面图片中泵房吸水干管与水池引入管的连接形式会产生气囊吗?

请问下面图片中泵房吸水干管与水池引入管的连接形式会产生气囊吗?水池引入管比吸水干管高,吸水干管和水泵吸水管是同一标高。谢谢!




kanka_n_di | 2025-02-28 10:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

磨砂猴 2025-02-28 10:43 00 [回复]举报

你说的那个地方应该不会,但是图片圈出来的那个水泵吸水口会形成气囊。

报告队长 2025-02-28 14:39 00 [回复]举报

16K702,介质下往上进泵大小头顶平防气囊,上往下底平防液袋

胡胡203 2025-02-28 16:19 00 [回复]举报

上面是图集的做法,从你提供照片来看,在吸水管与吸水干管连接处以及水泵吸水口处均有产生气囊的风险

阿龙 2025-03-05 08:53 00 [回复]举报

变径连接时,应采用偏心异径管件管顶平接。