消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问我这个消防车道设计是否合适?


本次设计的是戊类的厂房生产电杆的,不是甲乙类厂房按照规范要求不需要设置环形消防车道,详见下图规范要求:,我现在仅仅是内侧算是长边吧设置了消防车道,而且东侧可以不算是消防车道只是没有回转车场,利用东侧路通过去,不知道这样设计是否可行?请各位哥哥们给个意见:合理吗这样设计。能通过审查吗,或者是我设计成下面的是不是更合适一点?


朱老弟 | 2025-02-24 12:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

落花为伊人 2025-02-24 12:57 00 [回复]举报

建规7.1.9消防车道应有两处与其他道路相连通

朱老弟   回复: 落花为伊人2025-02-25 10:54

西边可以出去,我是说不需要没一个建筑都要形成环路吧

0    0 [回复]举报

落花为伊人   回复: 朱老弟2025-02-25 16:20

不需要

0    0 [回复]举报

朱老弟   回复: 落花为伊人2025-02-26 12:14

甲乙类的估计都要在建筑周围环起来吧,像这个样子

0    0 [回复]举报

落花为伊人   回复: 朱老弟2025-03-18 07:22

你图上标注的都是戊类厂房,不需要过度设计,如果是甲乙类,间距与占地都需要重新核算,相应标准也会不一样

0    0 [回复]举报

又方又圆 2025-02-27 16:55 00 [回复]举报

后面的更合适,因为消防车道对应的登高操作场地的长度至少为建筑的一条长边。

建筑设计防火规范50016-2024(2018年版)

7.2.1 高层建筑应至少沿一个长边或周边长度的1/4且不小于一个长边长度的底边连续布置消防车登高操作场地,该范围内的裙房进深不应大于4m。     建筑高度不大于50m的建筑,连续布置消防车登高操作场地确有困难时,可间隔布置,但间隔距离不宜大于30m,且消防车登高操作场地的总长度仍应符合上述规定。

关闭

关闭

手机APP下载