消火栓手报指示灯闪烁频率高,是什么原因,消控室图显正常也没有报故障。


请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

无觅 2025-03-17 16:36 00 [回复]举报

1. 部分厂家设计为周期性自检闪烁(如1次/秒),若频率显著加快(如2~3次/秒),可能为设备内部程序异常。

2. 电源或线路干扰  电源电压不稳(如低于DC24V额定值);线路接触不良或受电磁干扰(如与变频设备共用线槽)。

3. 设备内部故障  LED指示灯驱动芯片损坏;电容老化导致充放电异常。

4. 通讯信号异常(隐性故障)  总线信号短暂中断或波动;设备地址码冲突(多发生在系统扩容后)。

EHS专家-DL 2025-03-31 15:54 00 [回复]举报

  1. 1、优先检查手报装置电源输入稳定性与电池状态‌;
  2. 2、重新紧固线路接头并清洁氧化触点‌;
  3. 3、替换同型号指示灯模块测试是否为硬件故障‌;
  4. 4、通过专业设备检测电磁干扰与环境参数‌。