消防沙箱配几把铲?

有规范说配2把,有规范说配3~5把,有没有权威的解释?

虎王小子 | 2025-02-07 10:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

小唐12321 2025-02-07 14:37 00 [回复]举报

消防规范没消防沙箱吧

消防资源网 2025-02-07 16:59 00 [回复]举报

 水电工程设计防火规范 GB50872-2014

11.5.3 砂箱的设置应符合下列要求:
        1 每个设置点处的砂箱不应少于两个;
        2 每个砂箱储砂容积不应小于0.5m³;
        3 每个设置点处应配备消防铲两把
        4 露天设置的砂箱应有防雨措施。


 风电场设计防火规范 NB31089-2016


5.4.3 每台室外主变压器、电抗器的砂箱设置应符合下列要求:
    1 每个设置点处的砂箱数量不应少于1个。
    2 每个砂箱储砂容积不应小于1.0m³。
    3 每个设置点处宜配备消防铲3把~5把
    4 露天设置的砂箱应有防雨措施。