消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

湿式系统各楼层的末端试水装置必须加装压力表和排水漏斗吗?相关规范是哪条。谢谢!

湿式系统各楼层的末端试水装置必须加装压力表和排水漏斗吗?相关规范是哪条。谢谢!

ShiLiHui | 2024-12-16 00:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

消防网友68723 2024-12-16 08:48 00 [回复]举报

每个报警阀组控制的最不利点洒水喷头处应设末端试水装置,其他防火分区、楼层均应设直径为25mm的试水阀。  末端试水装置应由试水阀、压力表以及试水接头组成。试水接头出水口的流量系数 ,应等同于同楼层或防火分区内的最小流量系数洒水喷头。末端试水装置的出水,应采取孔口出流的方式排入排水管道 ,

ShiLiHui   回复: 消防网友687232024-12-19 13:19

好的 感谢


0    0 [回复]举报

jinyanwu 2024-12-16 09:57 00 [回复]举报

个人意见,仅供参考:

根据如下规范和条款:

消防通规规定如下:


溜达呀 2024-12-16 11:25 00 [回复]举报

如果是这套湿式系统的末端试水装置,那必须有压力表和排水设施。

规范依据《消防设施通用规范GB55036-2022》4.0.6 每个报警阀组控制的供水管网水力计算最不利点洒水喷头处应设置末端试水装置,其他防火分区、楼层均应设置DN25的试水阀。末端试水装置应具有压力显示功能,并应设置相应的排水设施。

ShiLiHui   回复: 溜达呀2024-12-19 13:19

好的 感谢

0    0 [回复]举报

潘天坤 2024-12-16 12:06 00 [回复]举报

一般是每个湿式报警阀组的最不利点设置末端试水装置(每个报警阀组控制的最不利点洒水喷头处应设末端试水装置)

按防火分区和楼层划分的是试水阀(其他防火分区、楼层均应设直径为25毫米的试水阀),不属于末端试水装置

ShiLiHui   回复: 潘天坤2024-12-19 13:19

好的 感谢

0    0 [回复]举报

关闭

关闭

手机APP下载