消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

强电井,弱电井必须使用防火门吗?有规范规定吗?

      
消防资源网 | 2024-12-09 21:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

溜达呀 2024-12-09 23:36 00 [回复]举报

是的,必须设置。根据建筑设计防火规范(2018版) 6.2.9 建筑内的电梯井等竖井应符合下列规定:

    1 电梯井应独立设置,井内严禁敷设可燃气体和甲、乙、丙类液体管道,不应敷设与电梯无关的电缆、电线等。电梯井的井壁除设置电梯门、安全逃生门和通气孔洞外,不应设置其他开口。

    2 电缆井、管道井、排烟道、排气道、垃圾道等竖向井道,应分别独立设置。井壁的耐火极限不应低于1.00h,井壁上的检查门应采用丙级防火门。

  综上所述,强、弱电井属于电缆井,必须设置防火门

同同不同 2024-12-10 07:12 00 [回复]举报

建规

6.2.9  建筑内的电梯井等竖井应符合下列规定:
    1 电梯井应独立设置,井内严禁敷设可燃气体和甲、乙、丙类液体管道,不应敷设与电梯无关的电缆、电线等。电梯井的井壁除设置电梯门、安全逃生门和通气孔洞外,不应设置其他开口。
    2 电缆井、管道井、排烟道、排气道、垃圾道等竖向井道,应分别独立设置。井壁的耐火极限不应低于1.00h,井壁上的检查门应采用丙级防火门。
    3 建筑内的电缆井、管道井应在每层楼板处采用不低于楼板耐火极限的不燃材料或防火封堵材料封堵。
    建筑内的电缆井、管道井与房间、走道等相连通的孔隙应采用防火封堵材料封堵。

火通规

6.4.4 电气竖井、管道井、排烟道、排气道、垃圾道等竖井井壁上的检查门,应符合下列规定:
    1 对于埋深大于10m的地下建筑或地下工程,应为甲级防火门;
    2 对于建筑高度大于100m的建筑,应为甲级防火门;
    3 对于层间无防火分隔的竖井和住宅建筑的合用前室,门的耐火性能不应低于乙级防火门的要求;
    4 对于其他建筑,门的耐火性能不应低于丙级防火门的要求,当竖井在楼层处无水平防火分隔时,门的耐火性能不应低于乙级防火门的要求。


李勤 2024-12-10 11:57 00 [回复]举报

关闭

关闭

手机APP下载