法兰静电跨接问题

石化罐区消防管线法兰需要静电跨接吗?

再笑 | 2024-11-27 17:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

阳明心 2024-11-28 08:38 00 [回复]举报

参考这个

13.2.12 在爆炸危险区域内的油品、LPG、LNG和CNG管道上的法兰及胶管两端连接处应有金属线跨接,主要是为了防止法兰及胶管两端连接处由于连接不良(接触电阻大于0.03Ω)而发生静电或雷电火花,继而发生爆炸火灾事故。在非腐蚀环境下,当法兰的连接螺栓不少于5根时,法兰连接处的连接是良好的,故可不做金属线跨接。

jinyanwu 2024-11-28 14:07 00 [回复]举报

消防管道走的是水,不需要进行静电跨接;

阳明心   回复: jinyanwu2024-11-29 08:34

虽然管子内部走的是水,但外部是石化罐区,属于爆炸危险区域,是否应该按照13.2.12的考虑。

0    0 [回复]举报

jinyanwu   回复: 阳明心2024-12-06 14:20

化工区域管道一般化学品存在很高的阻值,不容易导电,高流速下容易集聚电荷,形成放电,所以需要跨接;

水管道介质是水,多少都有杂质(除非是纯净水),导电性很好,所以管道一般不需要跨接即可。

冬天干燥环境喷水雾有时候目的就是消除静电。

0    0 [回复]举报